Sirius P.Eng.
Chemical
- Mar 26, 2019
- 26
We are currently designing a pressure regulating/let-down package for a natural gas pressure regulating and metering station (RMS) that consists of an active regulator, a monitor regulator and a safety shut-off valve (SSV) connected in series - in the direction of flow the SSV comes first, then comes the "Monitor Regulator" and then the "Active Regulator". The Active regulator is to be fitted with an electric actuator. Both the Monitor Regulator and the SSV are self-regulating.
In normal operation, the active regulator regulates gas pressure from 85 barg to 40 barg; while the monitor regulator and SSV are fully open. When the active regulator fails (in a fully open position), the monitor regulator, set at 42 barg, takes over the pressure regulation duty, and when that fails the SSV shuts (at 44 barg) to isolate and protect the low-pressure side from overpressure.
My colleagues and I have discussed at length these issues but I am not very certain and so would like to hear from the experienced and highly distinguished Engineers in this forum.
So here goes, in sizing the PSVs (to be placed downstream of the pressure regulators):
1. Is it double jeopardy to consider that both the active regulator and the monitor regulator fail in a scenario.
2. Is it double jeopardy to consider that both the monitor regulator and the SSV fail.
3. If (1) and (2) can be considered as double jeopardy, then what is/can be the justification for the provision of a PSV downstream of the regulators.
4. If a jet fire scenario is then found to be the governing overpressure scenario, what other means of effective overpressure protection may be provided against overpressure; bearing in mind that during exposure to a localized jet fire, failure can often occur due to localized overheating for which a PSV is ineffective (API 521). Other scenarios considered include blocked outlet and regulator failure - which was deemed not credible.
5. We found that in a similar project, the EPCC contractor did not take credit for the SSV and also did not consider the failure of the Active and Monitor Regulators as double jeopardy. Please share your ideas/experiences/concerns/comments/suggestions, etc.
In normal operation, the active regulator regulates gas pressure from 85 barg to 40 barg; while the monitor regulator and SSV are fully open. When the active regulator fails (in a fully open position), the monitor regulator, set at 42 barg, takes over the pressure regulation duty, and when that fails the SSV shuts (at 44 barg) to isolate and protect the low-pressure side from overpressure.
My colleagues and I have discussed at length these issues but I am not very certain and so would like to hear from the experienced and highly distinguished Engineers in this forum.
So here goes, in sizing the PSVs (to be placed downstream of the pressure regulators):
1. Is it double jeopardy to consider that both the active regulator and the monitor regulator fail in a scenario.
2. Is it double jeopardy to consider that both the monitor regulator and the SSV fail.
3. If (1) and (2) can be considered as double jeopardy, then what is/can be the justification for the provision of a PSV downstream of the regulators.
4. If a jet fire scenario is then found to be the governing overpressure scenario, what other means of effective overpressure protection may be provided against overpressure; bearing in mind that during exposure to a localized jet fire, failure can often occur due to localized overheating for which a PSV is ineffective (API 521). Other scenarios considered include blocked outlet and regulator failure - which was deemed not credible.
5. We found that in a similar project, the EPCC contractor did not take credit for the SSV and also did not consider the failure of the Active and Monitor Regulators as double jeopardy. Please share your ideas/experiences/concerns/comments/suggestions, etc.