Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

overheating of condenser from chiller unit

Status
Not open for further replies.

kingofelec

Electrical
Joined
Jul 18, 2013
Messages
6
Location
DZ
hello
we have a chilled water unit, this unit is installed outside in an environment where the ambient temperature is very high as there is a sandstorm
the problem is that the condenser of this unit is exposed to direct these changes ie the fins are not protected against excessive temperature and obstruction and fans operate continuously
my question is how to protect the condenser (it comes like that) against the overheating and there has equipment to add.
cordially
 
Lower the ambient temperature - except that you have no control over that.

Reduce the amount of heat that you are trying to reject.

Increase the amount of air you move through the condenser.
 
While you can't control the ambient temperature, you could shield the equipment from the sun, and you could clear away obstructions to air flow.

TTFN
faq731-376
7ofakss

Need help writing a question or understanding a reply? forum1529
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top