Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Overhead concrete with post-installed anchors

Status
Not open for further replies.

SrVaro

Structural
Oct 19, 2010
53
Should all overhead installations of post-installed anchors be considered cracked concrete?

My understanding has always been yes, but I cannot locate the source of this. Per ACI 318-08 appendix D (D5.2.6, D5.3.6, and D5.2.7), concrete can be considered uncracked where indicated by analysis. Thus, the above statement would not always be true.

While I think it would be best engineering judgment to assume cracked concrete. "Others" are disagreeing with me and want to use a not approved for cracked concrete anchor for an overhead application.

Does anyone have solid documentation one way or the other? In searching and re-reading previous posts it seems the consensus is to always assume cracked, but the "others" will not accept this so I need some good documentation.

Thank you.
 
Replies continue below

Recommended for you

Check out this link: Hilti pdf document link

It discusses cracked concrete a bit.

Also - in most concrete beams/slabs, under seismic loading you can get some pretty wild moment variations where typical gravity compression areas might go into tension.

 