- Jun 22, 2009
- 6
I would like to clear up some confusion I have with the proper sizing of fuses/wires for a simple Y-Delta motor starter configuration. I understand the concept of being able to use contactors rated at less than the motor horsepower/FLA and also about setting the overload relay to approx. 0.58% of FLA ( provided the overload relay is connected "inside the delta"). What I'm not sure about is if I can downsize the conductors on the load side of the contactors. The reason I ask, is that when I use a downsized contactor, the terminals often won't accept a conductor that was sized based on the full load motor current. However, by downsizing the conductors, it appears that they will no longer be adequately short circuit protected by the line fuses. I have attached a simplified connection diagram to help explain my confusion.
I would appreciate any input on this...it seems that I'm missing something obvious.
Dave
I would appreciate any input on this...it seems that I'm missing something obvious.
Dave