Assuming the NEC as governing code, the transformers are outdoors, and the building is indoors, and the transfer switch is not service rated; you need a breaker between the transformer and the ATS. A better application, next time, would be a breaker type ATS with a service entrance label, but given what it sounds like you have, you need another breaker.