parlitu,
As a general rule, motor life is directly related to temperature, but more specifically, temperature rise. As a rule, the winding insulation is based on a "normal" ambient of 40C, then there are different "Classes" of insulation that describe the overall rise above that which a motor will tolerate without loss of life expectancy. So without knowing what your Class rating is, there is no way to tell for absolute sure. Certainly, 15C air flow will help, but TurbineGen makes an excellent point about the rotor. Rotor temperature ratings tend to follow the stator insulation class they are used in, so depending on the type of motor enclosure design you have, that may not help. For example, if you have a TENV motor (Totally Enclosed Non Ventilated) with class A insulation, that 15C air stream may be insignificant because the rotor will never see it. In addition, a "rule of thumb" is that motor life expectancy decreases by 50% for every 10degC rise above the rated maximum temperature. So if you have Class B insulation, the max temperature is 40C, + 80C rise, + 10C hot spot, for a maximum motor temperature of 130degC. If you have no sensors embedded in the rotor to tell you what it's temperature is and that cool air never gets to it, you are taking a big chance in shortening the life of it.
TurbineGen,
Typically if someone describes their motors in kW rather than HP, they are not using NEMA rated motors and therefore they have no "Service Factor" as we know it. IEC motors tend to be the equivalent of what we would consider 1.0SF, especially those used in ventilation systems.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> faq731-376