UtilityGy
Electrical
- Mar 5, 2010
- 35
Gentelman,
My earlier post is related to the same equipment. While preparing a spec for a 27.6 kV outdoor breaker in a HV substation, I requested for vendors to provide me with a
velocity transducer point in front for motion testing using doble TDR3000. It is a standard for our utility. I beleive Doble has new models now like TDR9000 for the same test.
After talking to all vendors, It seemed like providing a point in front of breakers to connect a velocity transducer for doble testing for motion analysis is a thing of past.
Even after talking to our P&C techs, I found out that they dont bother with it during commissioning.
Is it classified as a design test now ?
I know you all as experts. Could you guys shed some light, Is motion analysis a must commissioning test. And if a point for attachment is required in front of circuit breaker for connecting Doble equipment.
I would appreciate an input.
My earlier post is related to the same equipment. While preparing a spec for a 27.6 kV outdoor breaker in a HV substation, I requested for vendors to provide me with a
velocity transducer point in front for motion testing using doble TDR3000. It is a standard for our utility. I beleive Doble has new models now like TDR9000 for the same test.
After talking to all vendors, It seemed like providing a point in front of breakers to connect a velocity transducer for doble testing for motion analysis is a thing of past.
Even after talking to our P&C techs, I found out that they dont bother with it during commissioning.
Is it classified as a design test now ?
I know you all as experts. Could you guys shed some light, Is motion analysis a must commissioning test. And if a point for attachment is required in front of circuit breaker for connecting Doble equipment.
I would appreciate an input.