hi Guys!
zicoo000 , As per NFPA-13 8.16.1.1.1.1, each sprinkler system shall be provided with listed indicating valve in an accessible location, so located as to control all automatic sources of water supply. Further, not necessarily you need a tamper switch but you must satisfy one of the requirement with reagrds to supervision. go through NFAP-13 8.16.1.1.2.
PS. NFPA-13 2010 ed.
hope it helps,