Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

os&y gate valve

Status
Not open for further replies.

zicoo000

Mechanical
Joined
Nov 26, 2013
Messages
15
Location
EG
At the base of each riser we put os&y gate valve and tamper switch ??????
please advice
 
you normally need an indicating control valve for the riser

does not have to be osy
 
You would have two OS&Y gate valve and in between them you would have a back flow preventer, at least in the USA.
 
I was of the opinion that the EPA did not want potential water supply contamination and therefore requiring all communities to have backflow preventers at least on new installations.
 
There are quite a few in this area that do not require a double check assembly. These AHJ's just require a single check on the riser or on the incoming fire line.

It surprised me as well when I moved to this area many years ago.

Travis Mack
MFP Design, LLC
 
hi Guys!

zicoo000 , As per NFPA-13 8.16.1.1.1.1, each sprinkler system shall be provided with listed indicating valve in an accessible location, so located as to control all automatic sources of water supply. Further, not necessarily you need a tamper switch but you must satisfy one of the requirement with reagrds to supervision. go through NFAP-13 8.16.1.1.2.

PS. NFPA-13 2010 ed.

hope it helps,
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top