I am just looking for some opinions on how other engineers deal with exterior mat foundations.
I have a cooling tower that is about 12 x 10 foot in plan. The frost line in our area is 30". I told the contractor to dig a 12x10 foot by 30" deep and pour a 3 foot thick mat.
I know that sounds excessive. But I believe that since it is exterior, a turn down does not gard against heave since the soil in the middle can heave. So rather than digging a 30" hole and filling it with compacted well drained rock, sloping the sides, and pouring a 12" mat with 30" inch turn downs, I say just fill it with concrete.
Concrete is cheap compared to fixing a tilting cooling tower. If it was a transformer or a generator pad, I would use a 12" mat with a turn down and let it go.
Thoughts?
I have a cooling tower that is about 12 x 10 foot in plan. The frost line in our area is 30". I told the contractor to dig a 12x10 foot by 30" deep and pour a 3 foot thick mat.
I know that sounds excessive. But I believe that since it is exterior, a turn down does not gard against heave since the soil in the middle can heave. So rather than digging a 30" hole and filling it with compacted well drained rock, sloping the sides, and pouring a 12" mat with 30" inch turn downs, I say just fill it with concrete.
Concrete is cheap compared to fixing a tilting cooling tower. If it was a transformer or a generator pad, I would use a 12" mat with a turn down and let it go.