Most manufacturers of 5-Way 3 Position valves mark the solenoids 12 and 14 and the ports are numbered
1= Inlet
2= Cylinder Outlet (Actuator Outlet)
3= Exhaust for Port 2 thru Port 3
4= Cylinder Outlet (Actuator Outlet)
5= Exhaust for Port 4 thru Port 5
Solenoid 12 shifts the valve to give flow from Port 1 to Port 2 and Exhaust's Port 4 thru Port 5
Solenoid 14 shifts the valve to give flow from Port 1 to Port 4 and exhausts Port 2 thru Port 3
Knowing the Port number connections allows the electrical programmer to energize the correct Solenoid to make an actuator perform the designated function.
I always draw the schematic so S12 makes a Cylinder extend or a Rotary Actuator turn Clockwise and S14 to make a Cylinder retract or make a Rotary Actuator turn Counter Clockwise.
With a Direct Solenoid Operated valve, energizing both solenoids at the same time will not change the valves position since that normally gives equal forces from the solenoids and equals no shifting will happen. However, most solenoids will overheat due to high Inrush Current and burn up quickly in this condition. The other possibility is the valve will shift since one coil acts faster and an actuator may operate but the opposing coil will fry due to high inrush current.
To protect the Solenoids always electrically interlock the signals so only one solenoid can be energized.
With Solenoid Pilot Operated valves equal Pilot Pressure to both sides of the valve keep it centered since fores are equal. However the Solenoids that shift the Pilot Section are not mechanically opposed so they operate normally without any damage.
Bud Trinkel, Fluid Power Consultant
HYDRA-PNEU CONSULTING, INC.