Thanks Cdafd & Travis. You guys always give brilliant response & Explanation. It really helped a lot. I am designing a Fire sprinkler system for Storage facility wherein I am using CMSA Sprinklers. Considering K-11.2 with 50Psi operating pressure for the remote sprinkler head, I am getting total inlet pressure to be 800psi(55bar approx.). Design area = 2000 sq.ft & total no. of sprinklers 16. Pressure seems to be too high but M going to discuss this with AHJ.
Cdafd, M mechanical Engineer working in Middle East.
Travis, Your example raises one more question. How you have minimum sprinkler demand pressure as 52 psi. It depends on total no. of sprinkler. right? If you consider 20 sprinklers then the pressure will go much higher than what you described.