txeng91
Structural
- Sep 5, 2016
- 180
I have been tasked with analyzing an existing composite floor system to support operable partitions Footprint is around 80x100 with composte bar joists spanning the 80’ dimensions between wf girders. They are wanting to add a significant amount of partitions, around 20 kips total, that will be supported by 6 joists, with the largest load a single joist is supporting around 10 kips or so. Big picture wise I see this as a relatively low risk modification since the joists are sized for 100 psf live load and the moment increase on the joists is typically in the 5%-10% raise. After many hours of calculations and research I think I can justify the additions with minimal stiffening, however I have a few concerns, see below:
1) The calculations I’ve obtained from the joist manufacturer (I’ve attached an example from one joist) show top chords and webs designed to capacity, with most the bottom chords and convections to the slab having quite a bit of extra capacity. One thing I don’t understand is that the axial load in the bottom chord is only a function of the total load and effective composite deck. My thought is that the axial load in the bottom chord should be calculated for pre composite load using the effective joist depth and the post composite load using the effective composite deck. The bottom chord would already be stressed prior to curing of the concrete and would maintain that stress based on the joist depth in addition to post composite stresses based on the composite depth. I have not been able to find any verbiage on this in SJI manuals.
2) The joists were originally designed in 1996 using ASD. The dead/live load split is about 50/50 so I am considering using LRFD in the analysis as this will give me around a 7.5% bump in capacity. The main reason for this is a lot of th truss webs were originally designed to 98%+ capacity and the partitions push many of them over 100% which would require stiffening. Any thoughts on this?
3) The max live load deflection will probably be in the 3”-4” range. On new construction I’ve done, manufacturers always have crazy deflection requirements like <1/2” andor L/1200. Has anyone had experience in retrofitting existing buildings witb partitions like this with high deflections and think this is doable?
Thanks for any responses
1) The calculations I’ve obtained from the joist manufacturer (I’ve attached an example from one joist) show top chords and webs designed to capacity, with most the bottom chords and convections to the slab having quite a bit of extra capacity. One thing I don’t understand is that the axial load in the bottom chord is only a function of the total load and effective composite deck. My thought is that the axial load in the bottom chord should be calculated for pre composite load using the effective joist depth and the post composite load using the effective composite deck. The bottom chord would already be stressed prior to curing of the concrete and would maintain that stress based on the joist depth in addition to post composite stresses based on the composite depth. I have not been able to find any verbiage on this in SJI manuals.
2) The joists were originally designed in 1996 using ASD. The dead/live load split is about 50/50 so I am considering using LRFD in the analysis as this will give me around a 7.5% bump in capacity. The main reason for this is a lot of th truss webs were originally designed to 98%+ capacity and the partitions push many of them over 100% which would require stiffening. Any thoughts on this?
3) The max live load deflection will probably be in the 3”-4” range. On new construction I’ve done, manufacturers always have crazy deflection requirements like <1/2” andor L/1200. Has anyone had experience in retrofitting existing buildings witb partitions like this with high deflections and think this is doable?
Thanks for any responses