Opening in One-Way Slab

Status
Not open for further replies.

ooox

Structural
Jun 22, 2009
95
I've been asked by a contractor if it's OK to cut a opening in a one-way spanning slab. Details are on the attachemnt and are as follows:

- 125mm thick, rebar not known
- spanning 3300mm from wall onto steel beam
- opening is 310x260mm at corner

I'm aware of rules governing the positioning and size of openings for 2 way spanning slabs however there seem to be very little on 1 way spanning slabs. My thoughts are rebar will be hit and the slab will lose some of its strength however due to the size and the location adjacent to 2 walls the slab will be OK with needing secondary steelwork or strengthening.

Any thoughts?
 
Replies continue below

Recommended for you

It is only 260 (10.5") in the direction that the slab is spanning, run a covermeter over it, the opening hopefully only cuts 1 bar maximum, it is in a low moment region so hopefully the slab with still have enough capacity in that region.

Is the wall running left to right along the page loadbearing?
 
I would not hesitate to cut the hole in this location. A crack could propagate from the corner, but it would be of no consequence.
 
I would prefer a circular hole for easy of coring, even so I wouldn't hesitate, just make sure they don't over cut too much.

When in doubt, just take the next small step.
 