I have an existing 8" cmu load bearing wall, I need to put a new opening ~6' wide. Typically I would use the detail with channels and squeeze the wall (or angles) but I need the finished product to be as close to flush as possible, the walls are not built out very much architecturally. The lintels would also need to be fireproofed.
I've been thinking about using a concrete beam instead of steel but have never done this, does anyone have experience with this? My thought is to place two channels above the future concrete beam w/through bolts frequently and squeeze the wall. I can then remove one course of block (or two if reqd.) below the channels, drop in bars, form up and pour. You wouldn't be able to completely pour it due to the channels/wall above but this could be grouted up with non-shrink after. The other option is to drop a precast beam in there and grout the gap on top. Once the concrete beam is set I can take out the channels and the wall below.
I also plan on inserting bars and grouting the cells adjacent to the new opening so I like the continuity of the rebar/grout on top of the opening as well as the sides.
This seems ok to me - it solves the fireproofing issue and leaves a flush/clean final product. Does anyone see any problems with it?
Thanks for your help
I've been thinking about using a concrete beam instead of steel but have never done this, does anyone have experience with this? My thought is to place two channels above the future concrete beam w/through bolts frequently and squeeze the wall. I can then remove one course of block (or two if reqd.) below the channels, drop in bars, form up and pour. You wouldn't be able to completely pour it due to the channels/wall above but this could be grouted up with non-shrink after. The other option is to drop a precast beam in there and grout the gap on top. Once the concrete beam is set I can take out the channels and the wall below.
I also plan on inserting bars and grouting the cells adjacent to the new opening so I like the continuity of the rebar/grout on top of the opening as well as the sides.
This seems ok to me - it solves the fireproofing issue and leaves a flush/clean final product. Does anyone see any problems with it?