I’m not sure I can come help with good solution, but maybe you can clarify:
Does a given CT enclose one phase of your three phase system or all three-phases?
Do you have one CT per phase?
What type of protection does this CT feed into ?
If it’s a differential, then as David as mentioned, it’s pretty good at detecting open already, but does rely on primary current flowing. If this is not acceptable for you (assuming it is a differential), you’d want to add your test current flowing through CT’s on both sides of the zone which accomplishes same thing as system current... will trip if one of CT’s opens.
=====================================
(2B)+(2B)' ?