Any suggestions on how to model open channel flow in a channel with zero slope and a drain located about halfway along its length? It is a unifomrly shaped asphalt channel.

Thanks
dpajr
 
Start with the critical point at the drain, that will give you a starting hgl for the flow rate you are evaulating
then I would use Manning's but each calculation will only be good for a short distance as the 'normal' level will increase to create at false slope the farther you get from the drain. eg there will be a slope in the hgl and egl but it changes as you get away from the drain.

Hydrae
 
Backwater effect.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
The use of a mannings equation will not help you in this scenario.

As msquared48 has said a backwater calculation is probably the way to go, however, you will have to consider how the flow is actually getting to the drain.

Looking at the smaller picture 0% slope= 0 conveyance....

You will probably have to consider a more broader approach considering the flow paths u/s of your area of interest, is there enough momentum u/s to actually carry the flow to your area of interest???? A RAS model may be the way to go...

Hope this helps.
 
Thanks to everyone for the quick response.
 
Mannings equation is for uniform flow. The situation you describe is classic "gradually varied" flow.
 
It can be modeled like a pond. Your flow would be a weir calc or an orifice depending on the head on the inv. Model it like a riser only scenario in your modeling software.
 
I would model it as a very large diameter tank (not necessarily cylindrical) with an orifice and let the surface area of the pond and flow thru the orifice vary with time.
 