11

Has anyone designed a one way 4" slab with dimensions 3 meter by 6 meter that is fully anchored in the long span 6 meter side (to beams) but one of the short span 3 meter side open? One way slab means the long span side is attached to the beam by top bars and continuous lower bars.
 
Replies continue below

Recommended for you

No, 4" is too shallow for a one way slab spanning 3m. Why are you mixing Imperial and metric units?

BA
 
Do you mean "No" meaning a 100mm slab can't be made one way? Or it can but "No" to the short span being open? Please clarify. Thanks.
 
There is nothing wrong with designing your slab as spanning in one direction, but I agree with BA that 100 mm is too thin for a simple span of 3 metres.
 

So for 100mm slab, it must be span in 2 directions or two-way.. meaning the long span of 6 meters and short span of 3 meters have to be both attached to the beams as in 2-way?
 
I wouldn't necessarily change the system, but would increase the slab depth.
 