Elie2
Electrical
- Aug 14, 2004
- 8
Hi,
I have 2 separate questions:
1. A project specifcations say that:
a. The transformer neutral shall be earthed to a bar, one tip of which linked to an earth pit and the other tip linked to the earthing ring around the premisses.
b. The neutral in the MDB shall be earthed (they say to help with the short circuit current quick trip of the breakers), it shall be earthed to a bar one tip of which is linked to an earth pit and the other to the earthing ring aound the premisses.
I do not want to do this for 2 reasons:
a. This creates an earth loop.
b. This causes all LN faults to become LE faults, but LL faults remain of the type LL. The breaker is a PACB Masterpact from Merlin Gerin equiped with a Micrologic 5.0 unit which does not sense faults to earth.
So am i right by not following these specifications?
Question 2:
I read somewhere that something needs to be done when feeder length become excessively long and become very resistive and reduce the short-circuit current which can delay the fuse or breaker disruption. I forgot what need to be done except that the solution with the software i use is to increase the size of the breaker. Please can you point me to NEC or other litterature about this in case i want to do something by hand or as per a table?
For those who use ETAP, we have a licensed station but the program is too complicated, any easy introductions?
Thanks.
I have 2 separate questions:
1. A project specifcations say that:
a. The transformer neutral shall be earthed to a bar, one tip of which linked to an earth pit and the other tip linked to the earthing ring around the premisses.
b. The neutral in the MDB shall be earthed (they say to help with the short circuit current quick trip of the breakers), it shall be earthed to a bar one tip of which is linked to an earth pit and the other to the earthing ring aound the premisses.
I do not want to do this for 2 reasons:
a. This creates an earth loop.
b. This causes all LN faults to become LE faults, but LL faults remain of the type LL. The breaker is a PACB Masterpact from Merlin Gerin equiped with a Micrologic 5.0 unit which does not sense faults to earth.
So am i right by not following these specifications?
Question 2:
I read somewhere that something needs to be done when feeder length become excessively long and become very resistive and reduce the short-circuit current which can delay the fuse or breaker disruption. I forgot what need to be done except that the solution with the software i use is to increase the size of the breaker. Please can you point me to NEC or other litterature about this in case i want to do something by hand or as per a table?
For those who use ETAP, we have a licensed station but the program is too complicated, any easy introductions?
Thanks.