I recently looked at a small two story apartment/residence. The building is a fairly simple rectangle with 2nd floor trusses spanning between exterior walls. It was built around 1980. There is a 2nd floor wall at mid-span of the trusses which supports attic joists. There was a crack in the 2nd floor ceiling. This happens where there is a flush header in the 2nd floor ceiling and likely overstressing the floor truss below the end of it.
However, the remainder of the second floor also slopes toward the center wall (i.e. the 2nd floor wood trusses are deflecting). The trusses are 12" deep spanning about 22.5' and deflecting about 1.0"-1.75" at the center.
There are a couple locations that I can see the 2nd floor trusses. The trusses are in fairly good condition and I don't see any issues with the plate connectors. My question:
While a repair is needed in the one location I mention above, it seems reasonable that the original trusses might be ok despite the excessive deflection.
A quick M/d = C = T gives a fairly reasonable value for compression even when carrying the interior wall. Could the deflection just be related to creep? Is the deflection reason enough to recommend reinforcing all trusses or putting an additional support below?
EIT
However, the remainder of the second floor also slopes toward the center wall (i.e. the 2nd floor wood trusses are deflecting). The trusses are 12" deep spanning about 22.5' and deflecting about 1.0"-1.75" at the center.
There are a couple locations that I can see the 2nd floor trusses. The trusses are in fairly good condition and I don't see any issues with the plate connectors. My question:
While a repair is needed in the one location I mention above, it seems reasonable that the original trusses might be ok despite the excessive deflection.
A quick M/d = C = T gives a fairly reasonable value for compression even when carrying the interior wall. Could the deflection just be related to creep? Is the deflection reason enough to recommend reinforcing all trusses or putting an additional support below?