structuralengr89
Structural
- Jun 28, 2006
- 108
I looked at an old metal building today where the owner wants to remove one of the gable end columns. The gable end wall paneling was removed and a new metal building was added next to the existing metal building. We discussed adding a new structural member and posting down with some new columns/footings.
I can come up with something that will work, but my question is about the existing construction. The end wall columns have a kl/r of over 300. I looked at the column capacity and the girder capacity and they both can handle about 19-20 psf of TOTAL gravity load for the roof. IBC Roof Live load reduction is 18.5psf. So that leaves the building with about 1 psf for all of the dead load.
I also noticed that the new metal building next to the old one had much larger member sizes for columns/beams that had fairly similar bay spacings.
I'm concerned about the liability and thinking about telling him to look elsewhere for advice. Thoughts?
Thanks!
I can come up with something that will work, but my question is about the existing construction. The end wall columns have a kl/r of over 300. I looked at the column capacity and the girder capacity and they both can handle about 19-20 psf of TOTAL gravity load for the roof. IBC Roof Live load reduction is 18.5psf. So that leaves the building with about 1 psf for all of the dead load.
I also noticed that the new metal building next to the old one had much larger member sizes for columns/beams that had fairly similar bay spacings.
I'm concerned about the liability and thinking about telling him to look elsewhere for advice. Thoughts?
Thanks!