NinerStruct
I recently started work on a site-adapt project for a public building that has already been used on another site. The structural engineer that did the previous design has since retired and I was tasked with the structural design of the new building. I rechecked the calcs from the previous engineer's design and did my own design when I couldn't find the original.
When redoing the design for a few columns, it appears that they were under-sized in the original design. The worst column is an HSS4x4x1/4 located in an area with a roof height of 19.5 ft, and a maximum unfactored design load of 62.5 kip. So my design says that it should be an HSS6x6x1/4" if there's no bracing provided.
The original building is over 10 years old now, and there hasn't been any failure. I'm guessing that's because a)it hasn't seen the full design load yet and b) the columns are buried in light gage walls that are likely providing some lateral bracing. Now, I don't imagine that the previous engineer had purposefully counted on non-structural walls to brace the column, but I can't find the original calcs for these. Either way, it's not something that I'm comfortable doing, so I'm changing them in the new design. Which leaves me with the question:
What should I do about the existing building with 4x4 columns already in service? Should I be notifying owner about this? Should we be coming up with a fix for these columns?