DavidCR
Mechanical
- Jan 10, 2002
- 359
Good day to you all.
We have two 5000 m3 (31000 barrels) aprox. fixed roof storage tank for diesel (Fuel Oil 2).
We need to specify fire protection based on foam chambers and water cooling to protect the steel walls from heat.
My question is about the water protection system.
We´ve checked the NFPA 15, which includes some criteria about the amount of water needed to delay the heating of the fuel. (The amount of water is huge for a tank like this, 0.25gpm/ft2).
A friend that works for an oil distribution company mentions that the protection of the fuel that they use (fixed systems) is provided by the foam system and it is complemented with water protection considering the steel plate structural resistance in case of fire exposure.
The water system he mentions consist of a pipe at the top that showers the tank with water, and provides protection for the steel in case of fire exposure and use 0.1 gpm/ft2 of exposed area. But he is not able to mention a code or bibliography to support this.
Can somebody please give some recomendations or comments about:
-design objetives and parameters for water systems like this,
-type of nozzles, sprinklers (I mean, is a central "shower" pipe enough?, I´ve seen it but also I´ve seen some photos of sprinkler rings around the tank.
-is NFPA 15 enough for this or other aproaches must be considered?.
Any comment will be appreciated, thanks a lot in advance.
David
Costa Rica.
We have two 5000 m3 (31000 barrels) aprox. fixed roof storage tank for diesel (Fuel Oil 2).
We need to specify fire protection based on foam chambers and water cooling to protect the steel walls from heat.
My question is about the water protection system.
We´ve checked the NFPA 15, which includes some criteria about the amount of water needed to delay the heating of the fuel. (The amount of water is huge for a tank like this, 0.25gpm/ft2).
A friend that works for an oil distribution company mentions that the protection of the fuel that they use (fixed systems) is provided by the foam system and it is complemented with water protection considering the steel plate structural resistance in case of fire exposure.
The water system he mentions consist of a pipe at the top that showers the tank with water, and provides protection for the steel in case of fire exposure and use 0.1 gpm/ft2 of exposed area. But he is not able to mention a code or bibliography to support this.
Can somebody please give some recomendations or comments about:
-design objetives and parameters for water systems like this,
-type of nozzles, sprinklers (I mean, is a central "shower" pipe enough?, I´ve seen it but also I´ve seen some photos of sprinkler rings around the tank.
-is NFPA 15 enough for this or other aproaches must be considered?.
Any comment will be appreciated, thanks a lot in advance.
David
Costa Rica.