Oil Preservation System for Transformers

Status
Not open for further replies.

Engineer1916

Electrical
Jan 9, 2020
42
Eng Tips Family,
Can you guys please give me any physical implications of choosing nitrogen blanket vs oil conservator for power transformers? I have a 50MVA transformer and I normally leave upto manufacturer to suggest the oil preservation system. But I am trying to understand the effects of 1 vs the other for example does the main tank size get bigger or smaller for oil conservator or nitrogen blanket etc. I hope I have explained it good enough.
 
Replies continue below

Recommended for you

The overall height including that conservator may taller with a conservator, while the main tank itself may be taller with a nitrogen blanket.
 
You have several options- 1) Nitrogen Blanket with automatic gas feeding 2) Conservator with free breathing through silica gel breather (conventional or automatic gel drying type) 3) Conservator with a flexible rubber balloon ( Atmoseal) and silica gel breather connected to pipe from inside of balloon 4) Conservator with a rubber diaphragm floating on the oil with breather over the diaphragm 5) Hermitically sealed unit with flexible tank/radiators to take the oil expansion.6) Conservator with refrigerant type breather. Disadvantage with (1) esp for EHV units is bubble generation during load changes. Today most popular option is (2) &(3)
 
If your HV is about 138kv or higher the height on the outline drawing is going to be set by the bushings, not the conservator space. Likewise at 50MVA I think the width/length is going to be set by the radiator space and the conservator will just sit above them.

Bill
 