oil filled transformer data

Status
Not open for further replies.

deltawhy

Electrical
Jun 1, 2011
95
Hi, I am starting to do some coordination work and I require some data. Does anyone know if you can get general oil-filled transformer data (%z, x/r, etc.) for units less than 5MVA without having to contact a specific manufacturer? This is for early design stage, which is why the exact transformer name plate info is not required. I've looked on google for a while without luck.

Thanks
 
Replies continue below

Recommended for you

Google for GE GET-3550F. Or contact a transformer manufacturer for typical data.
 
In the North American market, the standard impedance is 5.75% for kVA ratings greater than or equal to 500. The X/R is highly varible with values between 10 and 20. These values apply to 208 V and 480 V secondaries. See ANSI C57.12 for more details.
 