Apr 2, 2024 #1 gago03 Electrical Joined Apr 2, 2024 Messages 1 Location DZ hey ; after transformer oil degassing operation , should i measure the winding resistance insulation ? if yes what the standar
hey ; after transformer oil degassing operation , should i measure the winding resistance insulation ? if yes what the standar
Apr 4, 2024 #2 prc Electrical Joined Aug 18, 2001 Messages 2,019 Location IN It's not necessary. If you opened any current path or operated a tap-changer to wipe the contacts, then only winding resistance measurements need to be repeated. Upvote 0 Downvote
It's not necessary. If you opened any current path or operated a tap-changer to wipe the contacts, then only winding resistance measurements need to be repeated.