Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Office space electrical requirements 2

Status
Not open for further replies.

ss7stw

Military
Joined
Jan 13, 2004
Messages
2
Location
US
Is there a standard for general office space as far as power requirements....something like X amps per square foot of office space? Just a general rule of thumb for an office where people just have the normal things like a computer etc..
Same question for light manufacturing...any general rule?

Thanks
 
dear ss7stw,
Yes. It is of the order of 22 to 40 watts/sq m depending on the exact nature of office use. You can arrive at the amps from the voltage and an approx power factor of 0.8.
For more details just ask.
best regards,
 
This is something that may help.


One thing to look for is electric heat ( VAVs in particular ) and indivual loads such as elevators, UPS systems etc.

In general we use:
Lighting 3 va/Ft-Sq
Devices 2 va/Ft-Sq
HVAC 4-5 va/Ft-Sq
Misc 1.2 va/Ft-Sq

OR about 7-10 va/Ft-Sq

YMMV Your millage may vary. Location, usage,lighting fixture type, building insulation,heat source ( gas or electric) and amount of windows are factors to consider.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top