golf99
Electrical
- May 14, 2010
- 4
I have two gensets feeding a manual 3-pole xfer switch. It feeds an MDP which then feeds 8 SDPs. All 5 wire. 3-phase 4-wire and 1 Equipment grounding conductor. Genset 1 is bonded ,the other is not per the NEC. I have checked for an internal bond at genset 2 but dont get a continuity reading from neutral to ground. I have 8 amps on the EGC from MDP to SDP back to the gen set that is running. Nothing on the idle one. When i disconnect the 8 EGCs from the SDPs at the MDP I still have 3 amps back to the gen set. Why ? As I add the EGCs back on one at a time the current increases back to the 8 amps. The second issue I am now trying to identify is the source of the current coming from the trailers. I eliminated some misplaced bonding jumpers that created parallel paths. Also, the panels in the trailers are RCD protected rated at 30ma.. They are not tripping.. Induction from the phase conductors to ground wires ? Any help would be appreciated ! Thank you.