O86 Built up beam Moment Capacity

Status
Not open for further replies.

murphy89

Structural
Joined
Mar 24, 2022
Messages
17
Location
CA
Hello,

I am working through a spreadsheet written a number of years ago (probably early 2000's) by another engineer that calculates the number of plies of various lumber sizes to satisfy load, span, and bearing length criteria that I input.

One section of their spreadsheet under a title they call "Load Sharing" applies a factor of 0.9090909090 to the moment capacity of a built-up beam if there are 3 or more plies in the beam. I can't find any reference to this in my O86-2010. Is this something that used to be in the O86 code and no longer exists? Does anyone know?

Thanks!
 
Without seeing how it is specifically applied in the formula, it sounds like they're dividing by the system factor Kh of 1.1 for built-up beams. See Table 6.4.4 (that's in the O86-14 but I feel it's likely similar in the 2010). 1/1.1=0.9090909.
 
OMG, yes! that's exactly what it is. Thank you!
 