- Jun 16, 2012
- 5
Description: We have just recently installed a 480V, 560kW/700kVA diesel generator as an optional standby backup power for an existing building (single-line shown in the link below). The generator has a built-in 800A main CB, feeding a new Generator Dist. Board (main lug only). Three outgoing feeders are distributed in the bldg. feeding generator side of 3 new service-entrance rated ATSs. Each ATS has a built-in CB on its utility power side, because the existing dist. boards (on the secondary of existing 4160:480 or 4160:208 transformers in the bldg) were installed long time ago and didn't have a main, so we needed to provide them with a main for code-compliance. The ATSs are break-before-make (no paralleling with utility is allowed, and the 1-2 min. outage due to delay in transfer is acceptable for our loads).
Problem: Upon transferring the power from the utility to generator, one of the CBs in the Generator Dist. Board trips immediately. This 250AF/225AT CB is at the primary side of a new 150kVA, 480:208Y/120V transformer. It's a nuisance trip. The other breakers don't trip.
Suspected Root causes: (1) Transformer inrush: I verified the coordination study (TCC) and the inrush is 2200A @0.1Sec. The breaker has an instantaneous over-ride at 4000A @0.1Sec. So, it doesn't look like it trips due to inrush. (2) Governor poor frequency and/or voltage regulation causing surge current: The generator vendor strongly believes that this is not an issue with governor setting which has an electronic isochronous governor (we cannot change the settings to a higher voltage or frequency from generator control panel).
Other hints: The breaker did not trip without load on the secondary of the transformer downstream.
Any suggestions?
Problem: Upon transferring the power from the utility to generator, one of the CBs in the Generator Dist. Board trips immediately. This 250AF/225AT CB is at the primary side of a new 150kVA, 480:208Y/120V transformer. It's a nuisance trip. The other breakers don't trip.
Suspected Root causes: (1) Transformer inrush: I verified the coordination study (TCC) and the inrush is 2200A @0.1Sec. The breaker has an instantaneous over-ride at 4000A @0.1Sec. So, it doesn't look like it trips due to inrush. (2) Governor poor frequency and/or voltage regulation causing surge current: The generator vendor strongly believes that this is not an issue with governor setting which has an electronic isochronous governor (we cannot change the settings to a higher voltage or frequency from generator control panel).
Other hints: The breaker did not trip without load on the secondary of the transformer downstream.
Any suggestions?