Hi Punglu.
For my understanding only:
What do you mean 10% (primary) E/F setting, I start ?.
I really recommend to you, test again this relay, that unwanted triped.
If relay O.K., you have some E/F generation on this line.
Possible next variant, I see this case only once before about two years. E/F was on one line, but triped CB also on other substation. BTW E/F protection relays are connected to core balance CT and with NI curve.
We checked relays, settings, cables ( megger was O.K.), shields and after two days of work opened cable box and founded some signs of arcs
between phase and grounded. It was old SWG with many duct in
cable box, very hot day with 70% of hummudity.
This two parameters and overvoltages on the not faulted phases was resason of this unwanted trip.
Customer cleaned all cable boxes in this SWG and two years no problem, BTW in this plant within these two years was about 4-5 E/F fault and all of them in same place ( when first).
Regards.
Slava