Just to go back to the original post, which was basically Nuclear density gauges are not accurate. Well, from reading through all the posts (many times, including my own comments), I was struck by one fundamental comment which was missing, what level of accuracy (degree of certainty) is appropriate. The answer will be different for different projects and uses, which in turn should be reflected by the person/organisation writing the specification.
In principal, I believe that there are 3 types of specification which can be used on a project:
1. Method (how the work is done)
2. End product (minimum degree of compaction, max air voids etc...)
3.End performance (how the material needs to act, how stiff etc...)
Now depending upon the level of risk associated with a project/material/construction etc... this should be reflected in which type of or combination of specification should be adopted, and in the case of this post, how it should be measured and what equipment is suitable to measure it.
If the possibility of a method of measurement being less accurate (nuclear gauge) which in turn may causing an unacceptable risk, change the method. The fact that for bulk earth filling, method placement is often acceptable (with a limited number of tests to check the method is working), this should be reflected in the manner in which the check tests are conducted, hence in this instance density checks using a gauge are appropriate. If however a catastrophic failure could occur then surely the specification should account for this and alternative tests completed to check not only the method, but also the end-product and the end-performance.
When I write specifications, I will use site trials to prove the proposed method can achieve the end-product and end-performance. The contractor then has a target to aim for (end-product) and checks are done to ensure the end-performance is met. The level of accuracy of the test equipment can then be ‘built into’ the type and frequency of tests, plus the acceptability limits. In my own experience, if you do enough tests you will get outliers, if there are no outliers, someone has ‘normalised’ the data. An engineer should be competent to be able to assess this along with the implications on the design (my view, bit of a soap-box moment sorry). At the moment I spend a lot of time reviewing other organisations earthworks specifications and identifying the conflicting requirements within them followed by many hours taking to the various parties trying to find out exactly what the material needs to achieve. 95% compaction does not mean a soil is strong enough, nor will not settle/heave. Less than 5% air voids does not mean a soil will have sufficient shear strength. Just because a plate load test does not settle more than 25mm under a load of 240kN/m² does not mean the soil has an allowable bearing pressure of 80 kN/m². You have to look at the whole picture.
In summary, in my opinion a gauge can be accurate enough (when calibrated and in conjunction with other tests) for many projects, but each case is different and each should be assessed on a risk basis.