Hi, I'm hoping somebody can shed some light on a "field condition" of a 5.25"x11.875" PSL header. It has a holdown from above so it has an all-thread through it with a bearing plate on the bottom of the beam. The contractor notched in the 5"x5"x1/4" steel bearing plate, the notch is about 2" deep x beam width x 7" length. The beam span is 6.5' and the notch is 2.5' from the bearing end. The beam has a full length 1200 plf uniform load and 5800 lb point load directly over the notch (2.5' from end).
The header is in a 9' plate height wall. Siding is on, window is installed (only retrofit available seems to be on the interior face).
I know per NDS this condition is not allowed per Figure 3C - Notch Limitations for Sawn Lumber Beams. And I am extremely concerened about the stress concentrations and potential failure due to the notch.
I called TJI and they said they treat their PSL beams the same as sawn lumber for notches.
1) does anybody know of a way to determine the capacity of the notched beam?
2) does anybody know of a way to alleviate the stress concentration (possibly using a steel side plate sistered to the beam?)
Thanks in advance for any help!
The header is in a 9' plate height wall. Siding is on, window is installed (only retrofit available seems to be on the interior face).
I know per NDS this condition is not allowed per Figure 3C - Notch Limitations for Sawn Lumber Beams. And I am extremely concerened about the stress concentrations and potential failure due to the notch.
I called TJI and they said they treat their PSL beams the same as sawn lumber for notches.
1) does anybody know of a way to determine the capacity of the notched beam?
2) does anybody know of a way to alleviate the stress concentration (possibly using a steel side plate sistered to the beam?)
Thanks in advance for any help!