Assuming a cycle for the relay, 3 cycles for the breaker, and a cycle for margin, you can "save" a 15T fuse when you're far enough away from the substation to have your fault current below 430A (minimum melt). If you're willing to push your luck, you have to be below 575A at maximum clear. If you can get to a 140T, those numbers go up to 4500A and 5800A.
In that case I think the change from expulsion to non-expulsion is a more viable approach. Under the highest risk level we block reclosing and if the feeder trips it has to be 100% patrolled prior to reenergization. In that case we want to blow the fuse, if possible, and leave the feeder energized. The non-expulsion fuse is one tool to get there. Another tool is the S&C TripSaver, or equivalent. Those are useful in that we can put them in a one-shot definite time trip and then leave a margin above them and have a faster than normal "fuse blowing" scheme at the feeder breaker. Larger multi-phase taps have problems with both of those approaches, at least at 13kV.