According to ABS Building and Classing Marine Vessels (MVR) 4.8.2, clause 7.13.2, the normal and emergency lighting systems must be independent of each other and designed in such a way that a failure in one system does not cause the other to become inoperative.
Considering this requirement, how should the typical power distribution be configured to comply with the clause? Additionally, does the following arrangement meet the criteria?
We provide emergency lighting fixtures with integral battery backup:
1. Emergency lighting fixtures are powered by the Emergency Distribution Board.
2. The Emergency Distribution Board normally receives power from the Normal power source.
3. In the event of Normal power failure, the Emergency Generator activates and supplies power to the Emergency Distribution Board.
4. During the transition from Normal power to Emergency power, the integral battery within the fixture powers the emergency lighting fixture.
Does this configuration satisfy the requirements of the clause?
Depends.
In many places the battery inside the fixture lasts long enough to satisfy the requirements.
first find out what it has to do to meet your minimum time period for emergency lighting.
The typical integral e-light battery is specified to last 90 minutes. 46CFR requires 120 minutes. Good luck finding a fixture with an integral battery that lasts 120 minutes.
Sure, but with better seat belts ;-)
I just thought it was interesting that there was "Normal power failure" so there ought to be "Abnormal" power failure as well.
TTFN (ta ta for now)
With LED lights there seems to be a lot now with three hours duration.
120 minutes can be achieved but it's going to require some creative specification. There isn't an on the shelf option.
Luckily, there are no rules with regards to foot candles in the maritime regulations. You only need a bulb that turns on. Whether or not it illuminates anything is up to you.