Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Non-rated non-bearing interior partition intersecting a fire wall

Status
Not open for further replies.

Alberto57

Civil/Environmental
Joined
Aug 15, 2011
Messages
2
Location
US
Does a non-fire rated, non-load bearing interior partition intersecting a tenant separation wall (2 hrs) has any fire rating requirements?
The interior wall is free standing and will only end at the tenant separation wall, they will not be mechanically connected.
There is nothing in IBC regarding this situation, but it is very common.
Any help will be appreciated.
 
It's difficult to answer such a broad question without knowing the adopted building code, the occupancy classification on both sides of the wall, the building construction type, and if the building is protected by an automatic sprinkler system.
 
The code is the IBC 2007 edition, occupancy is mercantile on both sides, type of construction VB, and it is protected by sprinkler both sides.
 
Why is separation even required? The 2-hour wall isn't required.

There is no such thing as the 2007 IBC, unless this is a state code.

I'm having a hard time wondering why the 2-hour is an issue. What's the building area? Is their lot line issues?
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top