I'm assuming the wind loading is a mistake since it's an interior wall. The loading should come from Chapter 13 of ASCE 7-05. Calculated Fp according to equation 13.3-1, 13.3-2, and 13.3-3. Per Table 13.5-1 ap should be 1.0, and Rp should be 2.5. Also pay attention to footnote B of the table if the wall is braced by a wood diaphragm...
I'd distribute the seismic as a uniform pressure and design the wall on a 1-foot basis. Size the reinforcing as you would for any other lateral load on a wall (similiar to cantilevered beam).