non-fault current at the ground grid

Status
Not open for further replies.

jettme

Electrical
Jun 13, 2010
1
good day!

im having a problem regarding to new established substaion(115kV/34.5Kv), after its energization, current of 40amps has been read at actual test(located at the A-frame structures that holds the 115Kv Line), and also the ground conductors of the ground grid has current readings of 30+Amps, the problem now is how to locate the source of the current. can you give me some tips on how to detect it?

thanks

 
Replies continue below

Recommended for you

Do you have a place to read zero-sequence line current? Perhaps a microprocessor relay or a meter. The ground current might be because of unbalanced load current.
 
Hi, Jettem,

please loaded or unloaded line? what i understand it was not loaded.
please cofirm?

 
What's the transformer between the 115 and the 34.5? Is the 115 shielded? Probably lots of other questions to answer before you can get a useful answer, so it would be best to provide all details about the substation and all the lines in/out.
 