Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Non-contact Lap Slice Maximum Distance

Status
Not open for further replies.

NS4U

Structural
Apr 2, 2007
320
ACI 12.14.2.3 says that the maximum TRANSVERSE distance between lap bars in non-contact lap splices is ethier 1/5 the lap length or 6"

In a beam say, what is the "transverse" spacing? vertical spacing? Hoziontal? Both? It sounds to me that ACI was intentionally being vague
 
Replies continue below

Recommended for you

Transverse here means in a plane perpendicular to the direction of the bars (assuming your lapped bars are parallel to each other through the lap). If your bars are offset horizontally and vertically, then the transverse distance is on the diagonal.
 