I have an air handling unit in a mechanical room (surrounded by office space) whose walls are heavily insulated and has a baffle wall return air plenum to reduce noise transmittance. I am not concerned about the noise transmittance through the walls or baffle return. However, I am concerned about the noise transmittance through the supply ductwork.
At the fan discharge, the sound pressure is:
93 dB @ 63 Hz
95 dB @ 125 Hz
95 dB @ 250 Hz
89 dB @ 500 Hz
87 dB @ 1,000 Hz
78 dB @ 2,000 Hz
72 dB @ 4,000 Hz
67 dB @ 8,000 Hz
Because this is a low temperature (45 F) fan powered VAV system, we require additional insulation and have decided to use 1" sound lining (2 lbs/ft^3), 16 gage sheet metal (up to the first elbow outside of the mechanical room), and 1" external insulation (1.5 lbs/ft^3) to prevent condensation and reduce noise level. There is (1) 90 degree mitred elbow before the ductwork exits the mechanical room and the office space has a suspended acoustical ceiling.
My question is... Does anyone know where I can find USEFUL information to help in calculating the noise level I can expect in the office space based on the reduction from the elbow, sound lining, sheet metal, insulation, and SAC?
I am trying to stay away from duct silencers but still need to maintain an NC level less than 30 in the space. I would appreciate any information or suggestions you may have.
Thank you,
Steve
93 dB @ 63 Hz
95 dB @ 125 Hz
95 dB @ 250 Hz
89 dB @ 500 Hz
87 dB @ 1,000 Hz
78 dB @ 2,000 Hz
72 dB @ 4,000 Hz
67 dB @ 8,000 Hz
Thank you,
Steve