We have to deal with noise issues in valves all of the time, where we specify steam pressure reducing valves for district heating applications here in NYC. It turns out that for large flow rates the typical noise calculations show over 90dBa from the valve. If the valve is sized correctly with the right materials there is NO ill effects to the valve, these valves are designed for this type of pressure drop. It is the velocity in the valve that creates the drop in the first place, and noise is an unavoidable result.
However, as you can imagine, in a non-industrial setting, it gets LOUD. Normally the specification is for less than 80 dBa.
So, we use noise reduction techniques. There are valve trim options to mitigate the noise at the valve source, or orifice plates after the valve to break up the pressure drop to reduce the noise and also muffler devices after the valve that absorb the noise.