I’d like to ask if anyone knows why no-load loss of multi-winding power transformers is not referenced to the winding with the highest rated power as it is done with no-load current?
In IEC 60076-1 it is mentioned that no-load current, load-loss, and short circuit impedance can be referred to the highest/lowest rated power. At the same time nothing is said about no-load loss.
Have a look at the following example (form ABB handbook about testing of power transformers):
Power: 146,5 / 146,5 / 40 MVA
Voltage: 250 / 165 / 24 kV
Current: 338 / 513 / 962 A
Measured values during no load test: Uo = 24 KV / Io = 4,55 A / Po = 98,98 kW.
I understand how and why no-load current is expressed in % and referenced to the highest rated power resulting in Io = 0,129 %, but I do not understand why Po is left at 98,98 kW?
The same can be observed in Electron CAPE software where parameter “Magnetizing branch MVA” influences only no-load current.
Am I missing something?
Thank you.
I’d like to ask if anyone knows why no-load loss of multi-winding power transformers is not referenced to the winding with the highest rated power as it is done with no-load current?
In IEC 60076-1 it is mentioned that no-load current, load-loss, and short circuit impedance can be referred to the highest/lowest rated power. At the same time nothing is said about no-load loss.
Have a look at the following example (form ABB handbook about testing of power transformers):
Power: 146,5 / 146,5 / 40 MVA
Voltage: 250 / 165 / 24 kV
Current: 338 / 513 / 962 A
Measured values during no load test: Uo = 24 KV / Io = 4,55 A / Po = 98,98 kW.
I understand how and why no-load current is expressed in % and referenced to the highest rated power resulting in Io = 0,129 %, but I do not understand why Po is left at 98,98 kW?
The same can be observed in Electron CAPE software where parameter “Magnetizing branch MVA” influences only no-load current.
Am I missing something?