Marke wrote:
“The no load current is primarily magnetizing current and while there are no rules, there are trends.
Large high speed motors tend to have lower magnetizing currents than small or low speed motors.
In addition to the good information in the previous posts, the magnetizing current is dependent on the flux in the iron.“
I think its true. If we are talking about two similar large motors that are properly connected to the proper voltage and frequency, and have different no-load currents, we can ask: why?
One motor can have a no-load current 30% of the nominal current and the other 60%.
That's because the manufacturer wants to make a motor with greater power than the iron core allows. The reason is commercial in nature.
How can this be achieved?
Manufacturer enters the calculation with the maximum allowed (sometimes even higher) values for the air-gap flux density, which can cause excessive flux density in teeth and/or in back-iron.
Then tries to compensate this by increasing the insulation class, with increased ventilation,( high efficiency) etc, but sometimes these attempts are not entirely successful.
If we make the calculation of turns / coil depending on the dimensions of stator-iron for this motor with common values for the air-gap flux density, I am sure that the result would be higher (less power) , than the number of turn / coil which we have already in the this motor. This means that the manufacturer tried to get more power than we would normally expect. Often, such a motor is not designed for continuous operation at full load.
That's why I think it is desirable to keep the no-load current in normal limits.
A rough but satisfactory estimate, for large motors gave Electricpete:
“here are my general estimates for ratio of NLA/FLA for large motors:
Poles NLA/FLA
2 0.20
4 0.25
6 0.30
8 0.32
22 0.50”
Zlatkodo