teleski
Electrical
- Mar 2, 2007
- 1
I have a purged enclosure in a cl.1, div. 2 location. There is a 480v 3ph feed branching off to a control xfmr and several motor starters. The cabinet was designed that upon loss of purge, everything south of the secondary side of the xfmr is to drop out, removing the potential for the contactors to operate, but leaving the 480v feed intact. In my experience, the feed is usually brought to an external contactor. Upon loss of purge, all power to the enclosure is removed. not sure which direction to go with this...