Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

No. 18 Bar lap splice

Status
Not open for further replies.

asdf

Structural
Joined
Aug 17, 1999
Messages
63
Location
US
I have a set of plans that require lap splicing No. 18 bars. I have apprised the Owner that it is not allowed by code, however he commented that a professional engineered developed the detail, and he is satisfied that the lap splice is sufficient. Should I contest the issue any further? What is an appropriate tie spacing, and gauge of tie wire?
 
As you have alluded to, ACI 318 12.14.2.1 prohibits lap splicing bars larger than #11 (with a few exceptions). The commentary cites a lack of experimental evidence for lap splicing large bars. It seems that if the owner's PE is showing something that is expressly forbidden, they would need to provide testing or documentation to back it up. If you believe that the issue presents a safety risk, it is your responsibility to follow this issue up with the appropriate authorities.
 
Absolutely agree with Taro.
 
...except that asdf is not in charge.

The engineer in charge (liable before the public) is the one that has to take such decision.

If the engineer in charge is satisfied, and asdf, whichever its role in the construction, is not, he may follow whatever procedure the law has to ensure the compliance with regulations and his indemnity, but in no case will diminish the authority of the one in charge till an injuction by one able body so orders.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top