SrChemE,
Based on your posting history, am I correct in assuming you are working in a TiO2 plant? You reference TiCl4 leaks, working with toluene, N2-purged star valves, and liquid Cl2. All of which are found in the front end of the TiO2 process, specifically the oxidation area. If I had to hazard a guess (but keep the details still general enough for discussion here), you are asking about a control valve that controls an N2 purge on a salt system in the oxidation area. Since N2 is nearby, you want to use that N2 to supply the actuator?
I would not do this. If I am correct in the above assumptions, this purge is located in a rather...sensitive...part of the process. I speak from experience when I say that introducing N2 purge into this area (which is commonly done), ALWAYS has the potential for backflow of the process into the N2 lines. I've seen this happen with a double failure, and with check valves not holding. In our case, the N2 system either was tied directly to process or was used for pump/valve packing purge. The valve packings/pumps started leaking out fumes, but that was limited in quantity due to the tightness of the packing.
If you put this N2 feed on the control valve, you have a direct exhaust path that could evacuate your process directly to atmosphere. Depending on the failure mechanism and the actuator design, you could have as much as an 1/8" exhaust hole for venting, which at process pressure will get the entire area into IDLH VERY quickly for CL2 or TiCl4 due to the valve constantly modulating and releasing material.
If this "control" valve is instead an on/off valve and not a positioning valve, then the risk is lower due to the valve not exhausting except when opening or closing.
As always in this area, even a minor change like this deserves proper scrutiny. Based on the specifics of your valve/actuator/process tie-ins, you may find this is a low risk or high risk. Either way, I think you should gather a PHA team to review this with exact details of the design. My personal feeling is this: If this is a positioning valve, do not do this. If this is an on/off valve that only vents when moving, then this may be okay with proper safety review.