Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Nidec Id 300

Status
Not open for further replies.

bigheadted

Electrical
Joined
Jul 22, 2005
Messages
53
Location
GB
Hi I am trying to program a Nidec id300 motor mounted drive so that the Analogue input it uses as reference can be selected as wither 4-20ma or 0-10v via a digital input can anyone give me any pointers with this i can see that the Input type is controlled by setting a number in to a parameter, but I don't understand how to change that number dependant on the state of an input ?
 
00.011=6, ADI1 voltage type
00.012=4, ADI2 4-20mA
00.014=0
00.035=0; DIO1 select ADI1/ADI2 as refference
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top