NFPA13 Single Interlock Pre Action Area of Operation

Status
Not open for further replies.

DTR1968

Mechanical
Joined
Jul 11, 2014
Messages
8
Location
GB
Hello All,

Can someone please advise if the requirement to increase the area of operation by 30% is applicable to Single Interlock Pre Action Systems?

I can see from the Code that it is a clear requirement for Dry Pipe and Double Interlock.

My application is a non storage environment and the deterction devices are rate of rise heat detectors and flame detectors.

Thanks

Dave
 
No increase required for a single interlocked system.

 
Single Interlock Preaction systems admit water into system piping upon operation of detection devices (NFPA 13-2013 7.3.2.1(1)). The heat and flame detectors will be more sensitive than the sprinklers, and will admit water into the piping before the sprinklers activate (7.9.2.8.1.1). The 30% design area increase for dry and DIPA systems is to account for the delay between sprinkler activation and water application onto the fire.



R M Arsenault Engineering Inc.
 
Gentlemen,

Thank you very much for the clarifications.

Dave
 
Yes. But, I do not believe you can use the QR reduction in a SIPA. I could be wrong, but that is my recollection.

Travis Mack
MFP Design, LLC
 