According to 2007 CFC Section 2306.3.2.2, mixing High Hazard Commodities with Class I-IV Commodities results in classifying the entire storage area as High Hazard. However, Section 5.6.1.2.3 of 2002 NFPA 13 states that we can use the protection requirements for the lower commodity class as long as there are (1) no more than 10 pallet loads of the higher hazard commodity, and (2) the higher hazard commodity must be randomly dispersed with no adjacent loads in any direction (including diagonally).
Does that mean loads of the lower class commodities as well, or that the higher hazard commodities can't be adjacent to each other?
Are there any other classification reductions under certain criteria?
The main question though is which code supersedes the other? This seems to be a direct conflict between CFC and NFPA.
Thanks!
Thanks!