You would need to calculate the Incident Energy based on the available fault current, arc duration, the working distance of the worker’s face and chest areas from a prospective arc source for the specific task to be performed etc. It's not switchgear though, so it's not likely going to be an issue. I'd be shocked (pun intended) if the HRC is greater than 0, which means PPE will just be:
Natural fiber (cotton/wool) long sleeve shirt & pants, safety glasses, hard hat, V-rated gloves.
More importantly now though, is the issue of doing it with the power on! If it is over 50V, technically you now have to get an Energized Electrical Work Permit. Seems silly for changing a lamp, but that's the way it is. Turn the light switch off and it's fine, you can do it naked. But if it's too dark to see if all of the other lights are off, you technically have an issue with changing lamps while enegized.